NMPC with EXTERNAL cost: QP failure (Status 4 / NaN) during setpoint stabilization of rotary inverted pendulum
I am implementing an NMPC (SQP_RTI) with acados for a rotary inverted pendulum (Furuta pendulum / ADIP). The goal is setpoint stabilization at the upright position:
x_ref = [0, π, 0, 0]   (arm=0, pendulum=upright, velocities=0)
The system runs in real-time on hardware (TwinCAT/Beckhoff PLC, 20ms sample time, N=50, IRK with 4 stages).
Problem
I have the suspicion that the problem is related to my wrapping. My reference for the pendulum is at π, which is exactly where atan2 wraps from +π to -π. When the pendulum approaches the reference and crosses this boundary, I think this is where the problem lies — but I am not sure.
What supports this suspicion: when I hold the pendulum manually at +170° (approaching π from below), the solver does not solutions. When I hold it at -170° (same physical distance from π, but on the other side of the wrapping boundary), the solver fails as well.
When using the following code the set-point stabilization works but the swingup does not work
ocp.cost.cost_type   = "LINEAR_LS"      # linear cost funkltion J =   = (x - x_ref)' * Q * (x - x_ref)+ (u - u_ref)' * R * (u - u_ref)
    ocp.cost.W   = np.block([[Q, np.zeros((nx, nu))],       # Gewichtung mit Q und R
                              [np.zeros((nu, nx)), R]])
    ocp.cost.W_e = P                                         # terminal penalty
    ocp.cost.Vx   = np.vstack([np.eye(nx), np.zeros((nu, nx))])
    ocp.cost.Vu   = np.vstack([np.zeros((nx, nu)), np.eye(nu)])
    ocp.cost.Vx_e = np.eye(nx)
    ocp.cost.yref   = np.concatenate([x_ref, [u_ref]])        # Referenz [x_ref, u_ref]
    ocp.cost.yref_e = x_ref
This is my current code. here the swing-up comes close to pi but then i get the error from above
My code # ---------------- ADS / Timing ----------------
AMS_NET_ID = "134.28.49.25.1.1"  # deine AMS-NetID
PLC_IP     = "134.28.49.25"      # IP der Steuerung
AMS_PORT   = 851                 # Standard-Port für PLC1
# ---------------- Encoder ----------------
ENCODER_CPR_ARM = 8192  # Counts per Revolution
ENCODER_CPR_PENDLE = 4096  # Counts per Revolution
UINT16_MAX = 65536  # 2^16 für UINT16 wrap-around
position = "down"
# Hilfsfunktionen: Wrap, Encoder delta, etc.
def center_y_on_ref(ax, y_values, ref_value):
    Skaliert die y-Achse so, dass ref_value genau in der Mitte liegt.
    if len(y_values) == 0:
        return
    dev = np.max(np.abs(y_values - ref_value))
    if dev == 0:
        dev = 1.0   # damit man etwas sieht
    dev *= 1.1      # kleiner Sicherheitsfaktor
    ax.set_ylim(ref_value - dev, ref_value + dev)
def convert_to_radiant(counts, cpr=8192, offset=0):
    angle_rad = ((counts - offset) / cpr) * 2.0 * np.pi
    return angle_rad % (2.0 * np.pi)   # <- wrap auf [0, 2π)
def handle_encoder_overflow(current, previous, max_value=65536):
    diff = current - previous
    # Überlauf nach oben (0 -> 65535)
    if diff < -max_value / 2:
        diff += max_value
    # Überlauf nach unten (65535 -> 0)
    elif diff > max_value / 2:
        diff -= max_value
    return diff
def counts_to_rad_delta(diff_counts, cpr=8192):
    return (diff_counts / cpr) * 2.0 * np.pi  # KEIN modulo!
def convert_to_minus_pi_and_pi(a):
    return ca.atan2(ca.sin(a), ca.cos(a))
# --- Für NumPy / echte Zahlen (Runtime) ---
def wrap_angle_np(a):
    return (a + np.pi) % (2.0 * np.pi) - np.pi
def bounds_symmetric_around_zero(deg):
    rad = np.deg2rad(deg)
    theta_min = -rad
    theta_max =  rad
    return theta_min, theta_max
arm_boundary_min, arm_boundary_max = bounds_symmetric_around_zero(10)
def bounds_around_180(half_width_deg):
    h = np.deg2rad(half_width_deg)
    theta_min_pos = np.pi - h   # z.B. 170°
    theta_max_pos = np.pi       # 180°
    theta_min_neg = -np.pi      # -180°
    theta_max_neg = -np.pi + h  # z.B. -170°
    return theta_min_pos, theta_max_pos, theta_min_neg, theta_max_neg
pendlum_boundary_min_pos, pendlum_boundary_max_pos, pendlum_boundary_min_neg, pendlum_boundary_max_neg = bounds_around_180(10)
# Model parameter
m1 = 0.09
m2 = 0.08
mh = 0.10
L_1 = 0.1492
L_2 = 0.1778
g  = 9.81
km = 0.0741
# NMPC PARAMETER und contrains
N        = 50
dt       = 0.02
T_sim    = 4
n_steps  = int(T_sim / dt)
U = 5
x_ref = np.array([0.0, np.pi, 0.0, 0.0])
x0    = np.array([0.0, 0.0, 0.0, 0.0])
u_ref = 0.0
Q = np.diag([20, 50, 1, 10])
R = np.diag([10])
B = np.diag([1e8])
# ------------------------------------logging---------------------------
t_history = []
x_history = np.zeros((4, n_steps + 1))
u_history = np.zeros((1, n_steps))
status_history = np.zeros(n_steps)
qp_status_history = np.zeros(n_steps)
u_opt_history     = np.zeros((N, n_steps))
fallback_mask = np.zeros(n_steps, dtype=bool)  # True = Fallback wurde genutzt
solver_time = []
twincat_time = []
error_history = np.zeros((4, n_steps))
# Terminal Cost (LQR)
A_down = np.array([
    [0.0,   0.0,   1.0, 0.0],
    [0.0,   0.0,   0.0, 1.0],
    [-77.7, 42.9,  0.0, 0.0],
    [57.5,  139.3, 0.0, 0.0]
B_down = np.array([[0.0], [0.0], [27.2], [18.4]])
C_mat  = np.eye(4)
D_mat  = np.zeros((4, 1))
Ad, Bd, _, _, _ = cont2discrete((A_down, B_down, C_mat, D_mat), dt, method="zoh")
_, P, _ = control.dlqr(Ad, Bd, Q, R)
# Acados Modell (CasADi symbolisch, nur für den Solver)
def build_acados_model():
    model.name = "adip"
    x = ca.MX.sym("x", 4)
    u = ca.MX.sym("u", 1)
    theta, alpha, theta_dot, alpha_dot = x[0], x[1], x[2], x[3]
    Force = u[0]
    denom = L_1**2 * (4*ca.cos(alpha)**2 * m2 - m1 - 4*m2 - 4*mh)
    theta_ddot = (
        -(1 / denom) * 2 * (
              2*L_1**2 * ca.cos(alpha)*ca.sin(alpha) * theta_dot**2 * m2
            - 2*L_1**2 * ca.cos(alpha)*ca.sin(alpha) * theta_dot * alpha_dot * m2
            + L_2*m2*L_1 * theta_dot**2 * ca.sin(alpha)
            + m2*L_2 * alpha_dot * L_1 * theta_dot * ca.sin(alpha)
            + m2*L_2 * alpha_dot**2 * L_1 * ca.sin(alpha)
            + 2*L_1 * ca.cos(alpha)**2 * ca.sin(theta) * g * m2
            + 2*L_1 * ca.cos(alpha)*ca.cos(theta)*ca.sin(alpha) * g * m2
            - m1*g*L_1 * ca.sin(theta)
            - 2*m2*g*L_1 * ca.sin(theta)
            - 2*mh*g*L_1 * ca.sin(theta)
            + 2*Force
    alpha_ddot = (
        (1 / (L_2 * denom)) * 2 * (
              4*L_1**2*L_2 * ca.cos(alpha)*ca.sin(alpha) * theta_dot**2 * m2
            + 2*L_1**2*L_2 * ca.cos(alpha)*ca.sin(alpha) * alpha_dot**2 * m2
            + L_1**3 * ca.sin(alpha) * theta_dot**2 * m1
            + 4*L_1**3 * ca.sin(alpha) * theta_dot**2 * m2
            + 4*L_1**3 * ca.sin(alpha) * theta_dot**2 * mh
            - L_1**3 * ca.sin(alpha) * theta_dot * alpha_dot * m1
            - 4*L_1**3 * ca.sin(alpha) * theta_dot * alpha_dot * m2
            - 4*L_1**3 * ca.sin(alpha) * theta_dot * alpha_dot * mh
            + L_1*L_2**2 * ca.sin(alpha) * theta_dot**2 * m2
            + L_2**2*m2*L_1 * alpha_dot * theta_dot * ca.sin(alpha)
            + m2*L_2**2 * alpha_dot**2 * L_1 * ca.sin(alpha)
            + 2*L_1*L_2 * ca.cos(alpha)**2 * ca.sin(theta) * g * m2
            + 2*L_1*L_2 * ca.cos(alpha)*ca.cos(theta)*ca.sin(alpha) * g * m2
            - L_1**2 * ca.cos(alpha)*ca.sin(theta) * g * m1
            + L_1**2 * ca.cos(theta)*ca.sin(alpha) * g * m1
            + 4*L_1**2 * ca.cos(theta)*ca.sin(alpha) * g * m2
            + 4*L_1**2 * ca.cos(theta)*ca.sin(alpha) * g * mh
            - ca.sin(theta)*g*L_1*m1*L_2
            - 2*ca.sin(theta)*g*L_1*m2*L_2
            - 2*ca.sin(theta)*g*L_1*mh*L_2
            + 4*Force*L_1*ca.cos(alpha)
            + 2*Force*L_2
    f_expl = ca.vertcat(theta_dot, alpha_dot, theta_ddot, alpha_ddot)
    xdot   = ca.MX.sym("xdot", 4)
    u_prev = ca.MX.sym("u_prev", 1)
    model.x           = x
    model.u           = u
    model.f_expl_expr = f_expl
    model.f_impl_expr = xdot - f_expl
    model.xdot        = xdot
    model.p           = u_prev
    return model
# Acados OCP Setup
def create_ocp_solver(x_ref, u_ref):
    ocp = AcadosOcp()      # create ocp object to formulate the OCP
    model = build_acados_model()          # set model
    ocp.model = model                     # set model
    nx = 4     # 4 states
    nu = 1     # 1 input
    x = ocp.model.x
    u = ocp.model.u
    u_prev = ocp.model.p
    ocp.dims.N = N
    ocp.parameter_values = np.array([0.0])
    ocp.cost.cost_type   = "EXTERNAL"
    ocp.cost.cost_type_e = "EXTERNAL"
    error_x = x - x_ref
    error_u = u - u_ref
    change_of_u = u - u_prev
    error_x[0] = convert_to_minus_pi_and_pi(error_x[0])
    error_x[1] = convert_to_minus_pi_and_pi(error_x[1])
    model.cost_expr_ext_cost   = error_x.T @ Q @ error_x + error_u.T @ R @ error_u + change_of_u.T @ B @ change_of_u
    model.cost_expr_ext_cost_e = error_x.T @ P @ error_x
    ocp.constraints.x0    = x0    # Anfangsbedingung
    ocp.constraints.lbu   = np.array([-3.5* km])
    ocp.constraints.ubu   = np.array([3.5* km])
    ocp.solver_options.tf                  = N * dt          # istdas richitg für mich ?
    ocp.solver_options.integrator_type     = "IRK"           # ERK, IRK, GNSF, DISCRETE           # Explicit Runge-Kutta     # Implicit Runge-Kutta   -> IRK benutzen
    ocp.solver_options.num_stages          = 4               # 1, 2, 3, 4 (Runge-Kutta Stufen)
    ocp.solver_options.num_steps           = 1               # 1 default, 2, 3, ... (mehr = genauer, langsamer)  Number of steps in the integrator.
    ocp.solver_options.qp_solver           = "PARTIAL_CONDENSING_HPIPM"    # PARTIAL_CONDENSING_HPIPM, FULL_CONDENSING_HPIPM, FULL_CONDENSING_QPOASES
    ocp.solver_options.hpipm_mode          = "BALANCE"       # SPEED_ABS, SPEED, BALANCE, ROBUST
    ocp.solver_options.qp_solver_iter_max  = 400             # 50, 100, 200, 400, ...
    ocp.solver_options.nlp_solver_type     = "SQP_RTI"       # SQP, SQP_RTI
    ocp.solver_options.nlp_solver_max_iter = 1               # 1 (RTI), 50, 100, 200 (SQP)
    ocp.solver_options.hessian_approx      = "EXACT"  # GAUSS_NEWTON, EXACT
    ocp.solver_options.regularize_method   = "CONVEXIFY"   # NO_REGULARIZE, MIRROR, PROJECT, PROJECT_REDUC_HESS, CONVEXIFY, GERSHGORIN_LEVENBERG_MARQUARDT # nochmka nachguckebn
    ocp.solver_options.levenberg_marquardt = 0.0  # adds an constant term to the hessain
    ocp.solver_options.reg_epsilon         = 1e-2            # 1e-3, 1e-4, 1e-6, ...
    ocp.solver_options.qp_tol              = 1e-2            # 1e-3, 1e-4, 1e-6, 1e-8
    ocp.solver_options.tol                 = 1e-2            # 1e-3, 1e-4, 1e-6, 1e-8
    ocp.solver_options.print_level         = 0               # 0 (still), 1 (iter), 2 (verbose)
    solver = AcadosOcpSolver(ocp, json_file="adip_ocp.json")
    return solver
# Hilfsfunktionen: Lösung auslesen / Warm-Start setzen
def get_solution(solver):
    """Komplette Trajektorie aus dem Solver auslesen – analog zu sol.value(X/U)."""
    x_opt = np.array([solver.get(i, "x") for i in range(N + 1)]).T  # (4, N+1)
    u_opt = np.array([solver.get(i, "u") for i in range(N)]).T      # (1, N)
    return u_opt, x_opt
def set_warm_start(solver, x_init, u_init):
    """Warm-Start setzen – analog zu opti.set_initial(X, x_init)."""
    for i in range(N):
        solver.set(i, "x", x_init[:, i])
        solver.set(i, "u", u_init[:, i])
    solver.set(N, "x", x_init[:, N])
# ----------------Initialisierung ----------------
plc = pyads.Connection(AMS_NET_ID, pyads.PORT_TC3PLC1)
plc.open()
enc = plc.read_by_name("GVL.Enc")
prev_EncCounter_Ch1, prev_EncCounter_Ch2 = enc[0], enc[1]
plc.write_by_name("GVL.Motor_value", 0) # Motor auf 0 setzen
# MPC Closed-Loop Simulation
print("Starte MPC-Simulation ...")
x_init_warm = None
u_init_warm = None
counter = 0
planned_u = np.zeros((1, N))
planned_x = np.zeros((4, N + 1))
for i in range(N + 1):
    planned_x[:, i] = x0
solver = create_ocp_solver(x_ref, u_ref)
try:
    while counter < n_steps:
        counter = counter + 1
        t0 = time.perf_counter()
        time_twincat_1 = time.perf_counter()
        # Encoder auslesen
        EncCounter_Ch1, EncCounter_Ch2 = enc[0], enc[1]      # raw value
        time_twincat_2 = time.perf_counter()
        twincat_diff = time_twincat_2 - time_twincat_1
        twincat_time.append(twincat_diff)
        # Winkel berechnen
        arm_angle = convert_to_radiant(EncCounter_Ch1, ENCODER_CPR_ARM)   # encoder Daten zu Radiant
        pendle_angle = convert_to_radiant(EncCounter_Ch2, ENCODER_CPR_PENDLE)  # encoder Daten zu Radiant
        if abs(wrap_angle_np(arm_angle) - np.pi) < np.deg2rad(10):
            print("Pendelwinkel = π erreicht. Schleife wird beendet.")
            break
        arm_angle_pi    = wrap_angle_np(arm_angle)
        pendle_angle_pi = wrap_angle_np(pendle_angle)
                        # Anfangsbedingung prüfen (nur im ersten Schritt)
        if counter == 1:
            ARM_TOL_DEG    = 5.0   # ±5° Toleranz für Arm
            PENDEL_TOL_DEG = 5.0   # ±5° Toleranz für Pendel
            arm_deg    = np.rad2deg(arm_angle_pi)
            pendel_deg = np.rad2deg(pendle_angle_pi)
            if abs(arm_deg) > ARM_TOL_DEG or abs(pendel_deg) > PENDEL_TOL_DEG:
                 print("Pendelwinkel Fehlerhaft.")
                 break  # finally-Block übernimmt plc.write + plc.close
        # Differenz mit Überlauf-Behandlung berechnen
        diff_EncCounter_Ch1 = handle_encoder_overflow(EncCounter_Ch1, prev_EncCounter_Ch1, UINT16_MAX)
        diff_EncCounter_Ch2 = handle_encoder_overflow(EncCounter_Ch2, prev_EncCounter_Ch2, UINT16_MAX)
        # Winkelgeschwindigkeit berechnen
        omega1 = counts_to_rad_delta(diff_EncCounter_Ch1, ENCODER_CPR_ARM) / dt
        omega2 = counts_to_rad_delta(diff_EncCounter_Ch2, ENCODER_CPR_PENDLE) / dt
        # Aktueller Zustand
        x_current = np.array([arm_angle_pi, pendle_angle_pi, omega1, omega2])
        x_history[:, counter - 1] = x_current
        error_x = x_current - x_ref
        error_history[:, counter - 1] = error_x
            # Anfangsbedingung setzen
        solver.set(0, "lbx", x_current)
        solver.set(0, "ubx", x_current)
        for i in range(N):
            solver.set(i, "p", np.array([planned_u[0, i]]))
        solver_1 = time.perf_counter()
        solver.solve()
        solver_2 = time.perf_counter()
        solver_time_current = solver_2 - solver_1
        solver_time.append(solver_time_current)
        status = solver.status
        qp_status = solver.get_stats('qp_stat')
        if status == 0:
                # Erfolgreich: Neue Lösung auslesen und anwenden
                u_opt, x_opt = get_solution(solver)
                u_apply = np.clip(float(u_opt[0, 0]) / km, -U, U)
                input = -1 * u_apply * 555.556
                motor_value = int(input)
                plc.write_by_name("GVL.Motor_value", motor_value)
                # Trajektorie für den NÄCHSTEN Schritt vorbereiten
                planned_u = np.hstack([u_opt[:, 1:], np.zeros((1, 1))])
                planned_x = np.hstack([x_opt[:, 1:], x_opt[:, -1:]])
                # Warm-Start und Logging nur bei Erfolg
                u_opt_history[:, counter - 1] = u_opt[0, :] / km
        else:
            # Fallback: Solver hat keine Lösung gefunden
            print(f"Schritt {counter}: Solver Status = {status} -> Nutze Fallback!  u_apply = {u_apply}   " )
            # Gespeicherte Trajektorie weiter nach links verschieben
            planned_u = np.hstack([planned_u[:, 1:], np.zeros((1, 1))])
            planned_x = np.hstack([planned_x[:, 1:], planned_x[:, -1:]])
            fallback_mask[counter - 1] = True
            u_opt_history[:, counter - 1] = planned_u[0, :]
        # Status loggen
        status_history[counter - 1]    = status
        qp_status_history[counter - 1] = qp_status[-1]
        u_history[:, counter - 1]      = u_apply
        # Warm-Start für nächsten Schritt setzen
        set_warm_start(solver, planned_x, planned_u)
        # ---------- loggen ----------
        print(
            f"Schritt {counter} | Status={status} | "
            f"input = u={float(u_apply):+7.2f}| motorvalue= {motor_value:6d} | "
            f"θ1={np.rad2deg(arm_angle_pi):+7.2f} deg, "
            f"θ2={np.rad2deg(pendle_angle_pi):+7.2f} deg, "
            f"ω1={omega1:+7.2f} rad/s, "
            f"ω2={omega2:+7.2f} rad/s | "
            f"e_θ={np.rad2deg(error_x[0]):+7.2f}°, "
            f"e_α={np.rad2deg(error_x[1]):+7.2f}°, "
        # Update für nächste Iteration
        prev_EncCounter_Ch1 = EncCounter_Ch1
        prev_EncCounter_Ch2 = EncCounter_Ch2
        loop_dt = time.perf_counter() - t0
        print(loop_dt)
        t_history.append(loop_dt)
        time.sleep(max(0.0, dt - loop_dt))
except KeyboardInterrupt:
    print("\nProgramm beendet.")
finally:
    plc.write_by_name("GVL.Motor_value", 0)  # Motor ausschalten
    plc.close()
    print("PLC-Verbindung geschlossen.")